73:CP5511/5611 诊断测试后产生错误代码,代码的含义是什么?
0x0300 Cannot find module:
Please check whether the CP5511 is installed and slotted properly.
Check the interrupt and address assignments. Information on further procedures is available also in the STEP 7 Online Help under "Setting the PG/PC Interface", in the paragraph on "Checking the interrupt and address assignments". More information is also available in the STEP 7 Readme file ("Start > SIMATIC > Product notes"), in section 4.4.1 under "Built-in MPI onboard and the MPI PC module -> Setting interrupts and addresses".
0x0312 Incorrect configuration parameters: Deinstall the CP5511 and reinstall it again. For this you click the "Select" button in the PG/PC interface (Fig. 1). Mark the CP5511 with the cursor in the right window (Fig. 3). Then click the "Deinstall" button. Now, (after restarting STEP 7) you can mark the CP5511 in the left window and click the "Install" button. For this activity you need to have administrator rights to your PC (see STEP 7 Readme file, section 3.1).
0x0313 Baud rate does not correspond with network or incorrect interrupt:
Check the transfer speed (Baud rate) in the PG/PC interface and in the hardware configuration. The Baud rate must not be greater than the Baud rate that is supported by the slowest user. The PROFIBUS addresses configured in the hardware configuration must match the addresses of the system configuration.
Check the interrupt and address assignments. Information on further procedures is available in the STEP 7 Online Help under "Setting the PG/PC interface", in the paragraph on "Checking the interrupt and address assignments" (Index: Check interrupt assignment). More information is also available in the STEP 7 Readme file ("Start > SIMATIC > Product notes"), in section 4.4.1 under "Built-in MPI onboard and the MPI PC module -> Setting interrupts and addresses".
0x0316 Hardware ressource already busy:
If this error message occurs after the installation of the CP5511 in "Setting PG-PC interface
0x031a Cannot find any active PB/MPI network:
Activate the function "PG/PC is the only master on the bus" in the Properties of the PG/PC interface (see Fig. 4). This disables an additional safety function against bus faults. You get to this mask via the "Properties" button - see Fig. 1. The requirement is that the interface parameters used are set to "CP5511(MPI)".
0x0318 Interrupt occupied:
This message appears in most cases in Windows NT. In the BIOS of your computer change the "PnP" setting to "No". You get to the BIOS of your computer by restarting your PC and hitting the F2 key.
0x031b Synchronization error:
Please check the bus parameters on the bus. These must match the bus parameters configured in the hardware configuration.
Check the installation of the bus cable.
0x031c AMPRO2 system error:
Activate the function "PG/PC is the only master on the bus" in the Properties of the PG/PC interface (see Fig. 4).
Please check whether all the terminators for the PROFIBUS network are connected properly.
It is also possible that the STEP 7 drivers are not installed or have been deleted or that an incorrect driver has been installed. In this case we recommend sending the CITAMIS.str file to Customer Support for checking.
Another possible cause might be that the hardware is defective.
0x0320 Cannot find DLL/VXD as file:
On your PC please find the file specified in the Windows Explorer via "Tools > Find > Files/Folders". Either the file is not on your computer or it is found twice. Please rename the file in the Windows system directory and then restart Windows.
In the Registry, the references to the files are missing. Access to the required parameters from the Registry is not possible. Perhaps you don't have the required access rights or the system database is damaged.
PLC
The drivers are not compatible with the operating systems.