【摘要】 配电网采用环网结构、分段运行,是目前发展方向。双电源环网每条线路分3段的5组重合器供电方案,供电可靠性会更高,但该方案设备间的保护配合十分困难,向故障点多次短路冲击问题,一直未能很好地解决。文中提出解决这一问题的方法和运行经验,并总结了对单相接地故障段的选择或隔离,其方案具有较大的使用价值。
【关键词】 配电网 环网供电 运行分析
Abstract Looped network stracture under sectionalized operation is the current development trend on distribution systems. The scheme of double power sources with each line sectionalized into 3 sections and equipped 5 reclosers has been proved higher reliability. However,the coordination of protection among equipment is quite difficult,and problem of multiple short-circuit surge to faulty apot has not yet been solved for this scheme. this paper presents a method for solving these problems and their operational experience, and suggests a scheme for sclecting and isola-
ting the single phase to ground fault,which keing proved valuable.
Key words distribution grid looped network operational analysis
1 简述
随着城市建设的发展,用户对供电可靠性的要求越来越高,这就给原有配电设备的质量和配电网络的可靠性提出了更高的要求,而我国原有10 kV配电网大部分采用放射形供电,这种供电方式弊病较多,一旦某处发生故障,就会造成整条线路的大面积停电,且停电时间较长,可靠性差,为改变这种状况,最好的办法是近期采用环网接线,最终可采用网格式接线,正常时开环运行,这样的接线方式有一个以上电源向用户供电,从而大大提高了配网供电可靠性。
原能源电[1990]644号《关于加强城市中、低压配网改造的若干意见》指出:“架空配电网采用环网结构,开环运行,为缩小架空配电线路检修和事故时的停电范围,应装设分断开关,一般主干线分2~3段,装分断开关1~2台,较大的支线也应装断路开关,架空配电线路之间装设联络开关,以实现配电线路的互倒互带,提高运行的灵活性”。原能源电[1993]228号《城市电力网规划设计导则》4.4.8:“高压配电变电所之间的中压电网应有足够的联络容量,正常时开环运行,异常时能转移负荷”。
几年来,国内在配网自动化方面做了大量的研究工作,例如在自动化设备方面,先后从日本、英、美引进了DM系列自动开关,ERS型电子控制重合器和KFE系列重合器等,以上引进的各种设备在我国配电网中应用,取得了不少运行经验,但国外自动化程度较高的产品,并不一定适应我国配电网特点,为此在制造部门和供电部门的共同努力下,陆续开发出国产自动重合器、分断开关及环网负荷开关。目前由电力科学研究院引进英国ESR控制器研制的分布式自动重合器、FDKW型跌落式分断器;郑州凯特公司引进日本控制器研制的重合器、分断器;平顶山开关厂引进研制的美国COOPER公司KFE型重合器。配电网自动化设备是机电一体化的高技术产品,这些设备具有高压开关设备的基本性能,同时又满足智能化要求,这些产品的研制,促进了国内配电网自动化的发展,并通过不断总结逐步实现国产化。
配电网自动化方案方面,还需要做大量的研究工作。近年来,单电源放射形配电线路使用重合器、分断器配合的方案已较成熟;双电源环网每条线路分2段和3段组重合器方案运行也还算可靠,保护配合也能满足;如果双电源环网每条线路分3段的5组重合器供电方案,供电可靠性会更高,应该是更好的配网分段结构,但该方案设备间的保护整定十分困难,很难达到最满意效果。无论是每条线路分2段或3段,任一段发生永久性故障后,开环运行的主供电源侧和另一电源侧向故障点多次短路冲击问题,一直未能很好地解决。本文提出了解决这些问题的方法。
|